[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: New 8 second long 550 kV Power Arc
Original poster: John Keith <jskeith-at-interaccess-dot-com>
Hi Folks,
As a welder and a builder of power supplies, I have also done a lot of
experimentation in this area. A 200 Amp welder actually produces about 4-6
KVA due to the actual arc voltage being quite low, but your point is well
taken. The reason you get a long arc when quickly withdrawing the rod is
that the sudden decrease in current causes a corresponding brief
high-voltage pulse from the transformer. The xformer in an arc welder has a
high leakage reactance and behaves like a normal xformer in series with an
inductor. That's also why they are useful as ballasts for pigs;-)
Regards,
John K.
----- Original Message -----
From: "Tesla list" <tesla-at-pupman-dot-com>
To: <tesla-at-pupman-dot-com>
Sent: Monday, December 15, 2003 12:57 PM
Subject: Re: New 8 second long 550 kV Power Arc
> Original poster: DRIEBEN-at-midsouth.rr-dot-com
>
> Mike,
>
> It seems that you have done some experimentation in this area. I would
think
> that the idea of increasing the voltage with the amperage would apply too,
in
> this case. For example , a 200+ amp arc welder will easily put out 10 kVA
or
> more but I don't think your going to be able to pull a 3 ft. arc with your
> welding rod simply because the voltage is way too low (<50 volts). I have
> pulled out 6 to 8" of arc in this manor, though, by touching the welding
> rod to the work surface and quickly pulling the rod away ;^)
>
> It would be interesting to see the results of extensive tests in this
area.
> I agree, someone needs to get Bill Gates personally interested in HV ;^)
>
> David Rieben
>
> ----- Original Message -----
> From: Tesla list <tesla-at-pupman-dot-com>
> Date: Monday, December 15, 2003 9:01 am
> Subject: Re: New 8 second long 550 kV Power Arc
>
> > Original poster: "RIAA/MPAA's Worst Nightmare"
> > <mike.marcum-at-zoomtown-dot-com>
> >
> > Not sure about MVA levels (anyone know one of Bill Gates' phone
> > numbers so I
> > can test this?), but everything I've done from a 230 va obit to
> > 50 kVA
> > (actually was closer to 55 before the breakers popped and the
> > utility and
> > neighborhood complained) the 3.3-3.5 kVA/foot rule applies. In
> > think the
> > catch is to increase voltage along with current. With a 14.4 kv pig,
> > increasing current much beyond an amp actually stops the arc from
> > climbingas high up the ladder. Not sure, but seems to be blown out
> > with its own
> > magnetic field before long once it starts. I got around 17 feet
> > with 69 kv,
> > ~800mA. Unfortunately I sold the pigs when I moved from Stanberry
> > MO to here
> > in Cincinnati a few years ago. (The (2) 34.5 kv 25 kvA pigs
> > weighed over
> > 1000 lbs each, not something easy and cheap to move if you have no
> > garage to
> > put them in). I'm guessing as long as the voltage/current ratio
> > is around
> > 1A/50kv or so and a huge air mass was perfectly still (unlikely when
> > measured in miles) it's close to linear.
>
>