>>Dan and all,
>
>There are a couple of common styles of PT's used in the USA, and these will
>have different insulation ratings on the HV terminals. The first style has
>full insulation on both HV terminals, and is intended for line-line
>connection. Connecting this type in series can be done with no potential
>(no pun intended) problem since both HV outputs are rated at full Basic
>Impulse Level (BIL).
>
>However, the second style, used mainly in a sheltered substation or
>underground applications, may have only one HV terminal that is insulated
>for the full Basic Impulse Limit (BIL), since the PT is intended to be
>connected from line to ground. While this "ground" side HV terminal is
>still isolated from the core, it has a much reduced BIL rating (~10 kVRMS
>for a 14.4 kV PT).
>
>If you plan on using the second type of PT you MUST connect the terminals
>with the low insulation rating to the center ground point to avoid
>overvolting the HV winding.
>
>Best regards,
>
>-- Bert --
Hi Bert, all,
Bert is correct. I have (2) butyl rubber 7200 volt PTs.
One of them only has one HV bushing terminal while the
other has two. As I mentioned in an earlier post re-
garding this issue, I series the two together for 14.4
kVAC out to my HV rectifier for up to 20 kVDC to charge
my 10 kJ can crusher/quarter shrinker capacitors w/in
20 seconds. I run the single bushing one from ground and
take the "floating" 7200 volts off of the single bushing
of it and run it "piggie-back" to one side of the double
bushing one, making sure it's properly phased and get 14,400
volts out of the second PT's second bushing. I have had
no problems with this setup as I know the BIL rating of
both of the HV terminals of the second PT should easily
hold off up to 14,400 volts.