Re: [TCML] using an AC breaker for DC
In a message dated 9/9/08 1:37:07 P.M. Eastern Daylight Time,
nicothefabulous@xxxxxxxxxxx writes:
>The question is, can you safely use 125VAC-rated breakers on a DC circuit
for 72VDC in a solar
>power application as a battery disconnect? I told my brother that it was
harder for a DC arc to
>extinguish, but that I thought they would be okay as a disconnect.
Any DC ratings for the breaker will be in the manufacturer's
specifications. This includes fault-current interrupting capability, which will be much
lower with DC than AC and may be important with big batteries and big wire.
Time curves may differ with DC vs. AC, although I wouldn't expect by much.
Some manufacturers use the frames of their molded-case circuit breakers
as switch bodies. They just don't put in the "guts" that make the thing trip
(and it will be conspicuously labeled as a "switch" or "disconnect", and that
it has not tripping mechanism), I've seen these from Eaton/C-H for 120V DC
applications (for UPS applications).
The rated voltage of a breaker is going to be substantially lower for DC
than for AC. From Square-D, I can tell you that the QOx breakers for home
switchboards or panelboards are not going to be rated past 60VDC. You pretty
much have to get a breaker rated for 277VAC before it will even possibly be
rated for more than 48VDC. The larger frame breakers, including the I-Lines,
have some substantial DC voltage ratings, but always less than the AC rating.
I presume your breaker will be a "standalone", and not plugged into a
bus feeding DC branch circuits?
What are the exact manufacturer and model numbers of the breakers you're
looking at?
-Phil LaBudde
Center for the Advanced Study of Ballistic Improbabilities
**************Psssst...Have you heard the news? There's a new fashion blog,
plus the latest fall trends and hair styles at StyleList.com.
(http://www.stylelist.com/trends?ncid=aolsty00050000000014)
_______________________________________________
Tesla mailing list
Tesla@xxxxxxxxxxxxxx
http://www.pupman.com/mailman/listinfo/tesla